daestrom
Guest
Posts: n/a
|
"jclause" <(E-Mail Removed)> wrote in message news:(E-Mail Removed)... > In article <gt5Re.54058$(E-Mail Removed)>, > daestrom@NO_SPAM_HEREtwcny.rr.com says... >> >> >> >>Generally, a motor doesn't 'create' reactive power, we in the utility >>industry say that it 'consumes' reactive power. And a generator somewhere >>must 'generate' that reactive power. (reactive power can also be >>'generated' with other devices, but let's keep this simple) >> >>At a particular moment in the AC cycle, electrical energy from the >>generator >>is used to establish a magnetic field around a given set of windings in >>the >>motor. But later in the cycle, when that magnetic field collapses, that >>energy is re-induced into the windings as a short burst of electrical >>energy >>flowing *back* to the generator. On the next half-cycle, another bit of >>electrical energy from the generator is used to establish a different >>magnetic field around another set of windings, (or perhaps the same >>winding >>but with opposite polarity). Again, a short time later in the cycle, that >>energy is re-induced into the windings as another short burst of >>electrical >>energy flowing *back* to the generator again. >> >>So the 'reactive power' is a measure of the amount of energy that is >>flowing >>*back* and *forth* between the generator and a reactive load. >> >>To see this graphically, plot the voltage and current on the same X-Y >>axis. >>Pick several points through the cycle of the voltage, and multiply the >>instantaneous value by the instantaneous current value at the same moment >>in >>time. Most of the time, the results will be a positive number (either >>because both voltage and current are positive, or both voltage and current >>are negative). But for a small period of time in each half cycle, the >>product will be negative (because the voltage and current don't cross the >>x-axis at the same instant). This small negative portion is the reactive >>power 'flowing' back to the source. If you calculate the average of all >>the >>time the V*A waveform is above the axis, you will find it's average is >>*larger* than the 499.75 watts of 'real power' that is consumed in the >>motor. The excess is reactive power 'flowing' from the source to the >>load. >> >>For this energy to flow back and forth, you have to have an electric >>current. This current is 90 degrees out of phase with the applied >>voltage. >>When you combine this current, with the current associated with the 'real >>power' flowing from the generator to the motor, you get a total current. >>Because they are out of phase, you have to use some trig (or Pythagorion's >>theorem) to combine them. That's why you have (apparent power)^2 = (real >>power)^2 + (reactive power)^2. >> >>Now, if all the rest of the circuitry were 'ideal', then that would be the >>end of things. The generator puts a small amount of energy into the >>magnetic field of the motor, and the motor returns that energy to the >>generator a short time later (1/2 a cycle). >> >>But the conductors, wires and cables carrying all this current have a >>resistance. This dissipates power from the system in the form of I^2*R >>losses. To minimize losses, you want to minimize I and R. You can only >>do >>so much to minimize R for a given investment. You can minimize I by >>reducing the reactive load as much as possible. >> >>So, back to your example, the motor you describe is expending 499.75 watts >>of power in overcoming friction, I^2R losses in the resistance of the >>windings (not the connecting wires, just the internal windings), *and* in >>turning the shaft output connected to some load. The 332 'vars' is saying >>that 332 watts of power is flowing to and fro between generator and motor >>*every* 1/2 cycle. The combination of the two results in a total current >>of >>5A. >> >>To figure out the power dissipated in the lines between generator and >>motor, >>we have to know what the resistance of those wires is. Let us assume 1000 >>ft of 12 AWG copper wire (500 ft each way). That has a resistance of >>about >>1.64 ohms. So the power dissipated in the wire is (5A)^2 * 1.64 ohms = 41 >>watts. >> >>If we were able to correct the power factor *at the load*, then the total >>current could be dropped to just 4.16A (499.75w/120V). Then the total >>power >>dissipated in the same 500 ft feeder (1000 ft total wire length) would be >>just (4.16A)^2 * 1.64 ohms = 28.4 watts. >> >>On this scale, it isn't hardly worth it. But on a massive scale like a >>large industrial customer, the savings can be significant. >> >>Hope this helps... >> >>daestrom > > > Your answer is an example of what a tool the internet can be, as well as > the goodwill that should be more common. Thanks for your time and sharing > of knowledge. > > So the bottom line regarding power dissipated due to reactive power is > that it causes I^2 R power loss ln the lines above what that power loss > would be with a resistive load, i.e power factor = 1. Would this be an > accurate way to put it? > Yes. And to supply this extra current safely, requires slightly larger wires, breakers, and other equipment. There is an obvious tradeoff between correcting a very poor power factor (say, 0.3) to reduce the current-carrying requirements of the equipment, and correcting a 'nearly perfect' power factor (0.85). Sort of a 'guns & butter' economic tradeoff. > Seems to me that since reactive power causes additional current flow > above that required to produce real power, that it creates real power > in the lines going one way or the other at any given instant. However > since this real power received by the load during a half cycle is > returned to the source the next half cycle, then over a whole cycle it > sums to zero real power. Therefore it would require no extra energy from > the source above that driving the real power associated with the load. > And it doesn't. The only energy that has to be input to the generator shaft is the 'real power' needed to overcome I^2R losses, windage/friction in the generator *and* motor, and the motor output energy. Well, there *is* a little bit more energy needed in the generator's excitation system because a poor power factor (lagging) requires more excitation to maintain the generator output voltage. But nothing near the amount of power that is flowing back/forth every 1/2 cycle as vars. But a utility will get after a customer with a very poor power factor. Not because they require more *energy* (other than the increased I^2R losses), but because a large load with low power factor requires larger equipment, with larger current capacity for the same amount of kwh the utility sells. Given two customers, both using 1MW-hour a month, normally the utility would garnish the same revenue from each customer in the form of billable MW-hour's consumed. But if one customer has a 0.3 power factor, the utility has to maintain equipment that is three times the current capacity to supply that customer versus the customer with a 0.9 power factor. Larger transformers, transmission lines, extra voltage regulating equipment, fuse/breakers with higher capacity, all sorts of things (if it truly is a *large* customer). So the public service commission (or whatever regulatory body is responsible) allows the utility to levy an extra charge against the customer that has a very poor power factor. They recognize that such a customer represents a higher cost to the utility, and allow the utility to recoup those higher costs from that customer. And to avoid this extra charge, a customer may purchase their own 'power factor correction' equipment. With such equipment, the utility doesn't 'see' the poor power factor, and doesn't levy the extra fees. daestrom |
|
|
|
|
|||
|
|||
|
|
|
| |
![]() |
| Thread Tools | |
| Display Modes | |
|
|
Powered by vBulletin®. Copyright ©2000 - 2013, Jelsoft Enterprises Ltd..
SEO by vBSEO ©2010, Crawlability, Inc. |



Linear Mode