Re: Overhead Transmission Line System

 
 
SQLit
Guest
Posts: n/a
 
      08-30-2005, 04:36 PM

"magic" <(E-Mail Removed)> wrote in message
news:(E-Mail Removed) oups.com...
> Hi,
>
> Would you please find me why in overhead transmission line (HT)system
> there is no earthing line provided instead of Red, Yellow, Blue,
> Neutral lines.
>
> Appreciate if everybody give your opinion.
>
> Tks
>
> magic


I can not discuss every part of the world or the US for that matter. Medium
and High voltage transmission lines do not have an neutral, the small wire
that goes along is a ground/static line, in my experience. The static wire
may or may not be grounded to the pole or tower ground. I have seen it done
both ways. Most of the time the static line is there for lightning and it is
grounded to each tower/pole ground.
Earthing is only required on the transmission lines at the transformers.
The transmission lines are not in a wye configuration they are in delta. No
neutral.

Distribution lines/short distances are generally under 35 kv, considered
medium voltage in my neck of the woods. Transmission lines are generally
long distances and begin at 69 kv and go up from there.

Colors mean nothing. They are just a means of identification that the guys
installing it used.
When I was working on transmission lines we never used colors. Just id
numbers or names.


 
Reply With Quote
 
 
 
 
Beachcomber
Guest
Posts: n/a
 
      08-30-2005, 06:36 PM

>Earthing is only required on the transmission lines at the transformers.
>The transmission lines are not in a wye configuration they are in delta. No
>neutral.
>



Not exactly 100% true. There are many wye-delta and delta-wye
transformer connections in transmission lines. I believe the wye-wye
configuration is verboten due to harmonics, plus utility companies
don't like to send huge current through the earth as would be the case
with a grounded wye-wye with a significant imbalance in phase
currents.

Most transmission transformers have just one insulated bushing
insulator for economy. A delta connection would require two
bushings. Autotransformers (with no secordary) are also used.

Beachcomber


 
Reply With Quote
 
 
 
 
Don Kelly
Guest
Posts: n/a
 
      08-31-2005, 03:54 AM
----------------------------
"SQLit" <(E-Mail Removed)> wrote in message
news:tW%Qe.1443$(E-Mail Removed)...
>
> "magic" <(E-Mail Removed)> wrote in message
> news:(E-Mail Removed) oups.com...
>> Hi,
>>
>> Would you please find me why in overhead transmission line (HT)system
>> there is no earthing line provided instead of Red, Yellow, Blue,
>> Neutral lines.
>>
>> Appreciate if everybody give your opinion.
>>
>> Tks
>>
>> magic

>
> I can not discuss every part of the world or the US for that matter.
> Medium
> and High voltage transmission lines do not have an neutral, the small wire
> that goes along is a ground/static line, in my experience. The static wire
> may or may not be grounded to the pole or tower ground. I have seen it
> done
> both ways. Most of the time the static line is there for lightning and it
> is
> grounded to each tower/pole ground.
> Earthing is only required on the transmission lines at the transformers.
> The transmission lines are not in a wye configuration they are in delta.
> No
> neutral.
>
> Distribution lines/short distances are generally under 35 kv, considered
> medium voltage in my neck of the woods. Transmission lines are generally
> long distances and begin at 69 kv and go up from there.
>
> Colors mean nothing. They are just a means of identification that the
> guys
> installing it used.
> When I was working on transmission lines we never used colors. Just id
> numbers or names.
>


In general medium to high voltage overhead lines are supplied from a Y
source where the Y point is grounded,either directly or through impedance.
The "neutral" is the ground.
The use of delta for the supply of such lines is restricted to low voltage
and/ or short lines. A long line is capacitively coupled to ground and back
around 1920 or earlier, there arose the problem of ground faults which were
effectively undetectable but caused severe damage due to arcing. In
addition, passing charged clouds could and sometimes did, induce excessive
voltages on floating lines. Technically there are other advantages to
using a Y connected HV connection to overhead lines- these include cheaper
transformers, CT's, PT's insulation requirements, protective relaying needs.
In some distribution systems, delta was/is used, but in many places a
cheap way to handle increased load was to retain the lines and reconnect to
Y with existing distribution transformers switched from line to line to
line to ground.

Overhead static lines are grounded- in fact they are rather useless
otherwise. This may not be at every pole but the more ground connections,
the better.
--

Don Kelly @shawcross.ca
remove the X to answer


 
Reply With Quote
 
Andrew Gabriel
Guest
Posts: n/a
 
      09-02-2005, 08:58 PM
In article <tW%Qe.1443$(E-Mail Removed)>,
"SQLit" <(E-Mail Removed)> writes:
>
>"magic" <(E-Mail Removed)> wrote in message
>news:(E-Mail Removed) roups.com...
>> Hi,
>>
>> Would you please find me why in overhead transmission line (HT)system
>> there is no earthing line provided instead of Red, Yellow, Blue,
>> Neutral lines.

>
>I can not discuss every part of the world or the US for that matter. Medium


Yes, it really does help to say which country poster is interested in.

>Colors mean nothing. They are just a means of identification that the guys
>installing it used.
>When I was working on transmission lines we never used colors. Just id
>numbers or names.


Red, Yellow, Blue, are the 3 phase identification colours
in the UK (and some other countries which copy our scheme).

--
Andrew Gabriel

 
Reply With Quote
 
 
 
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
LCD overhead projector Mistubishi no light Roy and Rosa Electronic Repair 1 09-15-2005 10:02 PM
Fluorouscent lamp for Overhead projector losttoy2000@yahoo.co.uk Electronic Design 3 11-22-2004 05:53 AM
Buhl overhead projector focus adjustments Lenny Electronic Repair 1 10-28-2004 03:02 PM
Looking for data: Convex 806 Transmission Transmission Test Sets Rich Osman Electronic Equipment 0 03-07-2004 07:05 PM
Re: Alarm System and Home Automation FAQ - Overhead & Curtain Doors Robert Skinner Security Alarms 3 01-15-2004 10:52 PM