Re: Kitchen circuit suddenly reading 40V

 
 
Rich.
Guest
Posts: n/a
 
      03-07-2010, 06:55 PM

"Mike Reed" <(E-Mail Removed)> wrote in message
news:a9846d73-4b32-4d06-986d-(E-Mail Removed)...
>I plugged our vacuum in to the GFI in the kitchen, and when I turned
> it on, I heard a "pop" and assumed it was the GFI that needed to be
> reset for some reason. Well, the GFI plug was acting completely dead.
> I pulled it out of the wall, pulled off the line wires and tested them
> bare.
>
> 40V?!?!?!
>
> This circuit was fine this morning and has been installed for years.
> We recently remodeled and moved a couple plugs around, but they've
> been working fine for months (all on the GFI).
>
> The breaker goes both directions with a positive click just like the
> rest. This all started with the vac switch. I turned around and used
> the vac on a different circuit with no problem.
>
> Any chance someone's seen this before?
>
> Thanks!


Sounds like you have a second GFI outlet that was feeding this GFI outlet.
Look around to see if you can find another tripped GFI outlet. You also
might want to pull the panel cover and make sure you're getting full power
out of the breaker instead of assuming so based solely on the operation of
the handle.

 
Reply With Quote
 
 
 
 
Dean Hoffman
Guest
Posts: n/a
 
      03-07-2010, 10:52 PM
Rich. wrote:
>
> "Mike Reed" <(E-Mail Removed)> wrote in message
> news:a9846d73-4b32-4d06-986d-(E-Mail Removed)...
>> I plugged our vacuum in to the GFI in the kitchen, and when I turned
>> it on, I heard a "pop" and assumed it was the GFI that needed to be
>> reset for some reason. Well, the GFI plug was acting completely dead.
>> I pulled it out of the wall, pulled off the line wires and tested them
>> bare.
>>
>> 40V?!?!?!
>>
>> This circuit was fine this morning and has been installed for years.
>> We recently remodeled and moved a couple plugs around, but they've
>> been working fine for months (all on the GFI).
>>
>> The breaker goes both directions with a positive click just like the
>> rest. This all started with the vac switch. I turned around and used
>> the vac on a different circuit with no problem.
>>
>> Any chance someone's seen this before?
>>
>> Thanks!

>
> Sounds like you have a second GFI outlet that was feeding this GFI
> outlet. Look around to see if you can find another tripped GFI outlet.
> You also might want to pull the panel cover and make sure you're getting
> full power out of the breaker instead of assuming so based solely on the
> operation of the handle.


It turns out he had a bad connection at one of the upstream
receptacles. There was a burn mark at the connection. Someone
should've given the screwdriver another twist originally.
 
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need help with intermittent circuit failures - JK Flip Flops Jason S Electronic Basics 42 06-17-2006 12:50 PM
does this circuit use conventional current? Mike Electronic Basics 11 04-22-2006 04:06 PM
Re: Can somebody take a peek at this circuit for me? Larry Brasfield Electronic Basics 76 03-28-2005 01:15 AM
In Circuit PIC reading Paul \( Skiing8 \) Electronic Basics 1 02-21-2005 11:59 PM
Control of heater circuit part2 james Electronic Basics 24 04-19-2004 02:27 PM



1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93