"MPO" <(E-Mail Removed)> wrote in message
news:(E-Mail Removed) oups.com...
> I recently moved a small building to a ranch where there is no
> electricity service. The building had been connected to the power
> company and has a Service Entrance Panel on it. I want to connect it to
> a 5500 Watts 120/240 Volt Generator. The Generator has a bonded
> neutral. The neutral and ground are bonded at the Service Entrance
> Panel. Because the Generator has a bonded neutral and the Service
> Entrance Panel ground and neutral are bonded, my question is this.
>
> How should I connect the generator at the Service Entrance Panel?
>
> Since the Generator will be the only power supply I was trying to avoid
> buying a Transfer Switch. I was going to "unbond" the neutral and
> ground at the Service Entrance Panel and connect the 2 power leads,
> neutral and ground from the Generator to the corresponding connections
> on the Service Entrance Panel. Will this work or am I screwing up?
>
> Thanks for your help.
Does the generator have a overcurrent device? like a 2 pole breaker?
If it does then separate all of the grounds and neutrals in the service, and
drive a ground rod for the generator and run 2 hots and a neutral and ground
to feed the panel.
I would hesitate to tell you to unground the neutral at the genny as I do
not know how it is wound and doing that may be a problem for the generator.
As long as you do not have two sources of power you do not need a transfer
switch.
Some large weather proof twist lock plugs could be used for portability and
safety for the generator. ( if you take the genny with you it, will be less
likely to be stolen )
|