> PeterD wrote:
>
>> <(E-Mail Removed)> wrote:
>>>So it seems to be a case of it has to work, but it doesn't work. Any
>>>suggestions are welcome.
>>
>> You may have high resistance soil, and need more than one ground rod.
>> Code typically calls for three, wired together.
>
> I think you are probably right.
>
> A quick Google shows that multiple ground rods are often necessary.
> Although I found the NEC calls for multiple rods only when a single rod
> installation exceeds it says 25 ohms. And it seems that every other
> possible reason has been eliminated.
>
> --
> Tony Sivori
> Due to spam, I'm filtering all Google Groups posters.
I think I know what the problem is. In a house, at the electrical panel,
the neutral wire is connected to the ground. Your tester maybe assuming
this and that is why it is not showing a ground connection. Your generator
probably has a floating output (neutral not connected to the frame ground).
Which is why the tested shows no ground. This will not pose a problem when
using the generator, it is still grounded, it's just that the neutral is not
connected to ground.
Shaun