> What is the temperature of the melting point of insulation on mains
> flex which is made of silicone?
The immersion heater cable you can buy is, I believe, 180C max
operating temperature, but it's rubber (and I don't think silicone).
I'm not sure these have a 'melting' point, as the rubber is
thermosetting insulation, which will probably jusy go hard, and
eventually char or burn.
> Does anyone have a comparable figure for PVC insulation?
There are different types of PVC. The Twin and earth normally
used for wiring is derated to zero current at 70C ambiant, or
designed to operate at 70C at max current (whichever way you
want to look at it). IIRC, this allows for fault currents to
raise the temperature another 90C to 160C (in the time it takes
the protective device to trip), which is regarded as the max
momentary conductor temperature allowed before the cable sustains
instant permanent damage. So I presume it's above 160C but cable
is not designed to operate that hot other than in occasional
fault conditions.
Temperature affects the life in years of wiring too. At 70C,
you can expect PVC wiring to last around 23 years, whereas at
40C the life is (calculated) at 1,498 years. See:
http://www.iee.org/Publish/WireRegs/...pdateApr04.pdf
--
Andrew Gabriel