Wrong wrong wrong all.
A VFD can start the motor at 100% FLA. Starting restrictions are based
upon Across-the-Line (DOL) starting, where the starting current will
be 600% FLA. Using a VFD means there are NO RESTRICTIONS to the number
of starts per hour, other than those imposed by ramp settings. That is
true for both the drive and the motor.
Soft starters are another thing all together. The Starts-per-hour
rating of the motor stays exactly the same. Some soft starters, and
ESPECIALLY that Telemecanique piece of junk mentioned earlier, are so
cheaply built that they can take FEWER starts per hour than the motor
they are connected to. There are many brands that are built to exceed
the starts ratings of their motors, but that is not one of them. You
need to ask that question when selecting a soft starter, but many
people don't bother.
On Fri, 17 Jun 2005 17:12:44 GMT, "daestrom"
<daestrom@NO_SPAM_HEREtwcny.rr.com> wrote:
>
>"SQLit" <(E-Mail Removed)> wrote in message
>news:SLlse.75$9%(E-Mail Removed)...
>>
>> "BIGEYE" <address@is[invalid].ok> wrote in message
>> news:42b1d710$0$24474$(E-Mail Removed)...
>>> We have two submersible pumps (UK Spec) -
>>> Pump 1
>>> 250 kW, 4 Pole (1480 RPM), 690 Volts
>>>
>>> Pump 2
>>> 250 kW, 6 Pole (965 RPM), 690 Volts
>>>
>>> They are both controlled by inverters and typically the maximum speed is
>>> about 85% of nameplate speed.
>>> What is the maximum number of starts per hour for each pump.
>>> Appreciate if anyone can advise.
>>> TIA
>>
>> The manufacture would be the place to find out. Not knowing the service
>> factor of the motors and the loading it is only a guess.
>>
>> We have motors (larger) that we allow 3 starts per hour. All motors over
>> 250
>> hp are limited to 6 starts an hour. Per manufactures specs.
>>
>
>I'd be surprised if they allowed even six. IIRC, most motors of that size
>are limited to only 2 starts in three hours, or one restart if it was
>already up to temperature. Some really large units are limited to one start
>in 3 hours (these are MW range though).
>
>Of course, it depends too on the type of 'start'. A 'soft start' of an
>unloaded motor from a static inverter system might be very 'gentle' to the
>unit and be allowed any number of times. Also, if they had forced cooling
>(separate fans or circulating water). Or unusual insulation class...
>
>As always, the manufacturer would be the best place to start. But also look
>into the inverter design. 'Soft start' or VFD may be a lot more tolerable.
>(especially centrifugal pumps that have very low torque requirements at low
>speeds).
>
>daestrom
>
|