Don Bruder <(E-Mail Removed)> wrote:
> In article <(E-Mail Removed)>,
> Larry Hatch <(E-Mail Removed)> wrote:
>
>> Robert MacKinnon wrote:
>> > Hi,
>> > By chance I found two UPSes discarded in a rubbish bin. One of them, a
<snip>
>> > Can I parallel connect the APC batteries to the Powerware UPS to get
>> > extended standby time without having extra circuitry installed between the
>> > batteries?
>> >
>> >
<snip>
> Paralleling the batteries should *RUN* the critter fine, and extend your
Unless it melts due to lack of cooling.
> runnable time, but don't bet on the beast being able to keep all the
> batteries (however many that might end up being) properly topped off. I
> highly doubt that the charge circuitry is set up to handle keeping a
> proper charge on <insert some number greater than 1> batteries instead
> the single that it was most likely designed around.
If it's just a relatively simple constant current- constant voltage supply,
then it will, without any problem, it'll just take a lot longer to come up
to charged.
As batteries are charged over several hours, there probably won't be
any thermal issues on adding more.
If it's 'smart', then it may have a timer which cuts off charge, or
the software may be unhappy with the change.
--
http://inquisitor.i.am/ | private.php?do=newpm&u= | Ian Stirling.
---------------------------+-------------------------+--------------------------