Does anyone know of a single ic that will take a 4-20ma signal and
convert it to a 0-10 volt signal ???
It looks like someone would produce such a beast by now....but my
google searches have turned up nothing.
Tom Biasi
Guest
Posts: n/a
      03-21-2007, 01:08 AM
<(E-Mail Removed)> wrote in message
news:(E-Mail Removed) oups.com...
Can you settle for 2 to 10 Volts?
Paul E. Schoen
Guest
Posts: n/a
      03-21-2007, 01:25 AM
"Tom Biasi" <tombiasi@********optonline.net> wrote in message
news:BA%Lh.363$(E-Mail Removed)...
Yes, a 500 ohm resistor. Add a 2 volt battery and you have 0-8 volts. A 625
ohm resistor and a 2.5 volt battery (or offset) gives you 0-10 VDC.
Usually a 4-20 mA signal is a control loop which allows transducers to take
their power from the loop supply, and change the current according to what
they measure. The display can be as simple as an analog meter with the
pointer offset below the zero point, or can be an electronic digital
display powered from the loop. Power can come from any device in the loop,
or a separate battery or supply.
Paul
Jamie
Guest
Posts: n/a
      03-21-2007, 02:41 AM
you just use a voltage network to feed the transmitter from converter.
with this network, you can use an Op-amp with dual rail supply or
some negative offset to give you 0 volts at 4 ma's
something like a 24 DC supply using a 100 ohm Resistor to supply
the transmitter. The op-amp simply uses both inputs to monitor the
offset of the voltage on this resistor, which will translate to a
voltage output..
"I'm never wrong, once i thought i was, but was mistaken"
Real Programmers Do things like this.
http://webpages.charter.net/jamie_5
Anthony Fremont
Guest
Posts: n/a
      03-21-2007, 09:39 AM
A 1/2W 500 Ohm resistor will give you a 2V to 10V signal. You can use a
smaller resistor and an op-amp to not place so much load on the line.
Outside of using a resistor, you could measure the magnetic field coming off
the wire, but that's getting out there.
If you have to have 0-10V, you could do it something like this and use
another op-amp to double the voltage output:
http://pdfserv.maxim-ic.com/en/an/AN823.pdf
Chris
Guest
Posts: n/a
      03-21-2007, 09:53 AM
An operational amplifier is versatile and capable of performing the
conversion. Assuming you have a single 15V supply, here's an LM324-
based circuit that will do the job fairly well (view in fixed font or M
$ Notepad):
| VCC
| 12K| |
| '-' VCC
| .-. |\| Set For Vo = 0V
| 1K| |<-------|+\ at I(in) = 4mA
| | | | >-o--------.(1V)
| | | |/| | | ___
| === | GND | | .---|___|---.
| GND | | | | 25.5K |
| | ___ | |\ |
| + |\ '---|___|-o---|-\ |
| o----o-------|+\ ___ 10.2K | >----o---o Vo
|I(in) | | >-o--|___|-o-------------|+/
| .-. .---|-/ | 10.2K | |/
| 249| | | |/ | .-.
| | | | | 25.5K| |
| o----o |
| === GND
| GND
(created by AACircuit v1.28.6 beta 04/19/05 www.tech-chat.de)
The 249 ohm terminating resistor for your current loop will produce a
1 to 5 V input at the first op amp. The second op amp is supposed to
produce a 1.0V reference to subtract from the 1-5V. The resistors on
the third op amp are set up to provide a gain of 2.5 for the
difference -- 0-4V becomes 0-10V.
These are standard 1% resistor values. If you need/want 5%
components, try using 30K and 12K in place of the 10.2K and 25.5K. If
you need more accuracy, you might want to replace the LM324 with a
lower drift single supply quad op amp, and use a voltage reference
instead of your power supply to create the subtracting 1V.
Good luck
Chris
jasen
Guest
Posts: n/a
      03-21-2007, 11:35 AM
If you can live with a 2-10V output the "chip" is called a 500 ohm resistor
(2 1K resistors in parallel)
if that's not suitable something can probably be done using an op-amp.
Bye.
Jasen
MassiveProng
Guest
Posts: n/a
      03-22-2007, 01:26 AM
On Tue, 20 Mar 2007 21:25:46 -0400, "Paul E. Schoen"
<(E-Mail Removed)> Gave us:
There is 4 to 20mA NON-LINEAR range for instrumentation. There is
also
4 to 20mA LINEAR range for instrumentation.
Our IR thermometers offered 0 to 1 volt conversion as an option, but
I do not recall 0 to 10V.
Reply
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are Off
Similar Threads
Thread Thread Starter Forum Replies Last Post
using 12 volt battery with a 7.2 volt drill Mike Electronic Basics 10 08-06-2006 09:44 AM
Change ac volt meter to a dc volt meter mowhoong@hotmail.com Electronic Basics 3 07-03-2005 04:30 PM
Relay replacement: 150 volt coil down to 12 volt coil kc0atc@qsl.net Electronic Basics 4 03-08-2005 07:03 AM
12 volt to 48 volt DC quadrupler Andrea Zavareei Electronic Design 14 03-07-2004 08:04 AM
Is it ok to run a 24 volt trolling motor on a 12 volt battery to test the motor to see if it actually runs? SDNomad General Electronics 5 10-10-2003 05:56 PM